Why isn't point-to-point checkout done from the graphics?

By Bassirou Thiam, building automation engineer · Updated

Because the graphics sit on top of the control system. Point-to-point checkout proves that each wire, device and controller I/O works, even if everything above it failed. Checking from the graphics mixes two possible causes for every fault, the graphic mapping or the controller I/O, and needs a finished network first.

The right order

  1. Point to point: wire intact, landed on the right device, device sending and receiving the right signal, controller I/O configured. Points are forced by hand, ignoring the program and the graphics.
  2. Program: it matches the accepted sequence, including cases the sequence did not spell out.
  3. Graphics: top to bottom, every link checked and unused points removed.

Why the graphics still need a check

A sensor swapped on a graphic does not change how the program runs, so point to point at the controller will not catch it. Graphic mapping errors are found by checking the graphics themselves once they exist: once internally, then with the witness.

Sources

  1. Field discussion, r/BuildingAutomation: “Why is P2P not performed on graphics”
  2. Siemens, guide specification Section 23 09 00 – Building Automation System (submittals, network, point naming)